消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消防控制室

消防控制室中设置消防电话分机的作用是什么?是依据哪本规范哪条条款得出消防控制室需要设置消防电话分机

消防学徒 | 2025-04-14 16:23
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 6

EHS专家-DL 2025-04-14 16:34 00 [回复]举报

规范里规定的消控室设置的是消防电话总机外线电话啊。

《火灾自动报警系统设计规范》GB50116‌ ‌条款5.6.3.1‌:明确要求消防控制室需设置消防专用电话总机,并在消防水泵房、发电机房、配变电室等与消防联动相关的机房设置固定电话分机‌。‌条款6.7.5‌:规定消防控制室应设置可直接报警的外线电话,同时分机需分布在手动报警按钮、消火栓按钮等关键位置‌。‌《消防设施通用规范》GB55036-2022‌ ‌条款12.0.10‌:强制要求消防电话网络为独立系统,消防控制室需配置专用电话总机及外线电话,确保火灾时通信可靠性‌。‌

消防学徒   回复: EHS专家-DL2025-04-14 16:47

好的,谢谢。

但是我看到好多图纸上消控室都画了电话分机啊

0    0 [回复]举报

小唐12321   回复: 消防学徒2025-04-15 15:02

就问你总机设置在哪里,如果在这边还设计分机干嘛。

0    0 [回复]举报

大谧   回复: 小唐123212025-04-17 09:01

以前我也有这个疑问,但大的设计院给的方案都是在控制室单独设置一台消防电话分机。

0    0 [回复]举报

潘天坤 2025-04-15 09:30 00 [回复]举报

火灾自动报警系统设计规范 GB50116-2013第6.7.4条规定:消防值班室等与消防联动控制有关的且经常有人值班的机房应设置消防专用电话分机



法亦有道 2025-04-15 10:58 00 [回复]举报

根据火灾自动报警系统设计规范 GB50116-2013第6.7.4条规定:消防值班室等与消防联动控制有关的且经常有人值班的机房应设置消防专用电话分机。

请确认一下你说的是否是消防分控室。


关闭

关闭

手机APP下载