消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

临时高压消防系统,满足消防通用规范的条件不设置高位消防水箱的情况下,消防水泵需要满足一级负荷吗?

临时高压消防系统,满足消防通用规范3.09不设置高位消防水箱的条件,但是与消防给水及消防栓系统设计技术规范6.1.10.冲突,当室内临时高压消防给水系统仅采用稳压泵稳压,且为室外消防栓设计流量大于20L/s的建筑和建筑高度大于54米的住宅式,消防水泵的功底或备用动力应符合一级负荷要求供电。 应怎么执行?按上述条文,是指不设高位消防水箱时,消防水泵要按一级负荷吗?

aeiovf | 2025-03-29 11:10
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

满血复活中 2025-03-30 17:34 00 [回复]举报

是的,要按一级负荷供电。

根据《消防设施通用规范》GB 55036—2022 和《消防给水及消火栓系统技术规范》GB 50974—2014 的相关规定,当出现规范冲突时,应按照以下原则执行:

规范冲突解决依据

《消防设施通用规范》是强制性工程建设规范,自 2023 年 3 月 1 日起实施,其全部条文必须严格执行2。其中第 3.0.9 条规定了可不设置高位消防水箱的条件等内容。《消防给水及消火栓系统技术规范》是国家标准,其相关条文与《消防设施通用规范》不一致的,应以《消防设施通用规范》的规定为准。

具体执行方式

对于满足《消防设施通用规范》3.0.9 条不设置高位消防水箱条件的临时高压消防系统,当室内临时高压消防给水系统仅采用稳压泵稳压,且为室外消火栓设计流量大于 20L/s 的建筑和建筑高度大于 54m 的住宅时,消防水泵的供电或备用动力应符合一级负荷要求供电。这是因为在这种情况下,虽然不设置高位消防水箱,但为了确保消防系统的可靠性和灭火能力,需要对消防水泵的供电保障提出更高要求,以满足火灾时的消防用水需求。

条文理解

可以理解为在不设高位消防水箱且满足特定条件(仅采用稳压泵稳压、室外消火栓设计流量大于 20L/s 的建筑和建筑高度大于 54m 的住宅)时,消防水泵要按一级负荷供电。这样规定是为了在没有高位消防水箱提供初期消防用水和稳压的情况下,通过可靠的供电来保证消防水泵能及时、稳定地启动和运行,为消防灭火提供足够的压力和流量。

wetom 2025-03-31 09:06 00 [回复]举报

首先,要按一级负荷设置。其次,设施通用规范3.09条基本上就是消水规6.1.9条第一款的原文,6.1.10算是6.1.9条第二款的补充,怎么会冲突呢?

关闭

关闭

手机APP下载