请问预作用自动喷水灭火系统中快速排气阀前电动阀的动作信号是如何反馈至消控室火警主机的手动盘,致使手动盘上的反馈信号灯点亮的?具体怎么接线?

肖书 | 2025-03-28 15:14
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

EHS专家-DL 2025-03-31 10:03 00 [回复]举报

一、动作信号反馈逻辑

  1. 信号触发机制
    快速排气阀前电动阀开启后,其内部微动开关或位置传感器会生成‌无源常开触点信号‌,该信号通过输入模块(如监视模块)转换为可识别的通信协议‌。

  2. 信号传输路径
    输入模块通过‌消防二总线‌(如RS485或火灾报警专用总线)将信号传输至消防联动控制器,再由控制器将状态信息同步至消控室火警主机的手动控制盘‌。

  3. 反馈灯触发原理
    火警主机接收到输入模块上传的“电动阀已动作”信号后,自动激活手动盘对应按钮的‌反馈指示灯‌(通常为红色或绿色LED),实现状态可视化‌。


二、具体接线方式

  1. 电动阀端接线

    • 使用电动阀自带的‌无源常开触点‌(通常标注为COM、NO);
    • 将触点输出线(一般为2芯屏蔽线)接入输入模块的‌信号输入端‌(如S+、S-端子)‌。
  2. 输入模块配置

    • 输入模块需设置与火警主机匹配的‌设备地址编码‌;
    • 模块电源由消防系统DC24V专用线路独立供电(接L、G端子)‌。
  3. 手动控制盘关联

    • 手动盘的反馈灯通过‌内部逻辑编程‌与输入模块地址绑定;
    • 当主机确认信号有效性后,直接驱动对应指示灯电路‌