消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

镇中教学楼 背后 居民住宅楼 防火间距 某个 角落多处 小于 4米, 符合规范么?有什么依据符合规范?






















知耻也要问 | 2025-03-28 14:46
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

消防网友68723 2025-03-28 15:15 10 [回复]举报

两座建筑相邻较高一面外墙为防火墙,或高出相邻较低一座一、二级耐火等级建筑的屋面15m及以下范围内的外墙为防火墙时,其防火间距不限。
    3 相邻两座高度相同的一、二级耐火等级建筑中相邻任一侧外墙为防火墙,屋顶的耐火极限不低于1.00h时,其防火间距不限。
    4 相邻两座建筑中较低一座建筑的耐火等级不低于二级,相邻较低一面外墙为防火墙且屋顶无天窗,屋顶的耐火极限不低于1.00h时,其防火间距不应小于3.5m;对于高层建筑,不应小于4m。
    5 相邻两座建筑中较低一座建筑的耐火等级不低于二级且屋顶无天窗,相邻较高一面外墙高出较低一座建筑的屋面15m及以下范围内的开口部位设置甲级防火门、窗,或设置符合现行国家标准《自动喷水灭火系统设计规范》GB 50084规定的防火分隔水幕或本规范第6.5.3条规定的防火卷帘时,其防火间距不应小于3.5m;对于高层建筑,不应小于4m。

知耻也要问   回复: 消防网友687232025-03-31 18:14

关键是防火间距范围最短处附近:  教学楼有窗,周围住宅也有窗, 而且间距小于4米。套这个规范,套不上,解析不来。

0    0 [回复]举报

胡胡203 2025-04-01 17:51 00 [回复]举报

换甲级防火窗间距按3.5米满足吗?

vicher 2025-04-08 15:23 00 [回复]举报

多层建筑,可考虑按《建筑设计防火规范》5.2.2条注5处理。

关闭

关闭

手机APP下载