一个层高十几米的车间,设置丙类中间仓库。这个防火墙的分隔要做到梁下去高度实在太高,请教一下,有没有其它变通的办法呀?

消防网友44928 | 2025-03-21 14:52
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

小唐12321 2025-03-21 15:03 00 [回复]举报

上面打楼板可以不

重庆消防 2025-03-21 15:18 00 [回复]举报

没有变通方法,规范有明文规定。

EHS专家-DL 2025-03-21 16:19 20 [回复]举报

提以下三种思路供大家讨论看看是否可行?


方案一:局部降低中间仓库高度,分段设置防火墙

    将中间仓库设计为‌局部夹层或分层结构‌,仓库层高控制在常规分隔高度范围内(如6m以内)。在车间与中间仓库交界处设置‌分段防火墙‌,每段防火墙高度与夹层楼板衔接,避免通高分隔‌。夹层楼板需满足‌耐火极限≥1.5h‌,并与防火墙形成连续防火分隔‌;仓库与车间之间设置‌防火挑檐‌(耐火极限≥1.0h),防止火势通过顶部蔓延‌。


方案二:防火卷帘+防护冷却水幕系统

    在车间与中间仓库分界处设置‌特级防火卷帘(耐火极限≥4.0h)‌,替代部分实体防火墙‌。同步设置‌防护冷却水幕系统‌,覆盖卷帘及周边区域,确保火灾时卷帘背火面温度不超过规范限值‌。


方案三:独立防火隔间+水平分隔

    将中间仓库设计为‌独立防火隔间‌,四周采用耐火极限≥4.0h的防火隔墙(非承重墙)围合‌。在隔间顶部设置‌水平防火挑板‌(耐火极限≥1.0h),与车间顶部结构隔离,避免通高防火墙需求‌。防火隔墙需与车间主体结构脱开,避免火灾时因结构变形导致分隔失效‌;隔间内设置独立排烟系统,确保火灾烟气可控‌。

闲淡潮人   回复: EHS专家-DL2025-03-25 10:12

赞同第三种,比较方便实现

0    0 [回复]举报