消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

二类高层公共建筑是否需要设置火灾自动报警系统

各位大神需要技术支持,请问1栋二类高层公共建筑内设有自动喷水灭火系统和室内消火栓系统,其他消防系统未涉及,有独立的水泵房,需要设置火灾自动报警系统吗?

山城老头 | 2025-03-11 13:45
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

vicher 2025-03-11 14:18 00 [回复]举报

条件不明确,需根据建筑的使用性质、结合《建筑防火通用规范》第8.3.2条及《建筑设计防火规范》第8.4.1条要求进行判定。

潘天坤 2025-03-11 14:53 00 [回复]举报

楼主描述的不是很清楚,当设置在下列场所可能要注意:

1、如果此场所吊顶净高大于0.8m并且吊顶内存在可燃物,则此场所的吊顶内需要设置火灾自动报警系统的探测器;
2、如果此场所使用明火、燃气,则可能需要设置可燃气体报警装置;

3、如果二类高层公共建筑中存在建筑面积大于50平方米的的可燃物品库房和建筑面积大于500平方米的商店营业厅,那么此可燃物品库房和商店营业厅内应设置火灾自动报警系统;

4、如果此场所属于旅馆建筑/商店建筑/展览建筑/财贸金融建筑等需要设置火灾自动报警系统的建筑内,那么此场所应设置火灾自动报警系统


重庆消防 2025-03-12 09:20 00 [回复]举报

关闭

关闭

手机APP下载