稳压泵系统为什么应采用明杆闸阀

 消防给水及消火栓系统技术规范 GB50974-2014 5.3.5 稳压泵吸水管应设置明杆闸阀,稳压泵出水管应设置消声止回阀和明杆闸阀

稳压泵系统为什么应采用明杆闸阀

雄哥 | 2025-01-23 10:35
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

小唐12321 2025-01-23 11:09 00 [回复]举报

好看啊,巡检时候一眼就看出来关没关,你按照执行就好了

徐海金 2025-01-23 11:30 00 [回复]举报

1.好分辨有没有被关

2.明杆闸阀水头损失小,稳压泵管道本来就小,用其他的水头损失大。

喧哗 2025-01-23 11:53 00 [回复]举报

现在好多消防稳压设备厂家给配的都是蝶阀

小唐12321   回复: 喧哗2025-01-23 14:30

我觉得蝶阀几年后就很难关死,维修不方便

0    0 [回复]举报

雄哥   回复: 喧哗2025-01-24 11:29

是啊,设备厂家基本上都是配备手柄蝶阀,我们去检测或评估怎么判定,按规范吧,这是普遍现象,不按规范,出报告又无法规避风险

0    0 [回复]举报