走道挡烟垂壁设置疑问

不大于3米的走道清晰高度不宜小于净高的1/2,疏散净高度又要求不小于2.1米,挡烟垂壁如何设置较为合理。

| 2024-12-27 14:09
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 8

LHH2737 2024-12-27 14:21 20 [回复]举报

净高小于或等于3m时,排烟窗可计算按净高1/2计算,挡烟垂壁按不小于2.1m高且不小于500mm设置,不用纠结

  回复: LHH27372024-12-27 15:12

假设层高2.5米,清晰高度不宜小于1.25米,挡烟垂壁就算设置500毫米,疏散高度只剩2米。吊顶后层高小于2.6米的走道有点不友好,最近遇到两例。

1    0 [回复]举报

LHH2737   回复: 2024-12-27 15:27

这个目前还没有解决办法,只能在图面上写净高2.6m,挡烟垂壁按距地2.1m设置,验收时专家也不会去纠结这个,因为他也没有解决办法

1    0 [回复]举报

@2017年秋   回复: 2024-12-30 09:19

在建筑防烟排烟规范中4.6.9条    最小清晰高度=1.6+0.1H(排烟空间的净高度)     然后+500的挡烟垂壁   就是最小的吊顶净高度

0    0 [回复]举报

SUNNY@ 2024-12-27 16:17 00 [回复]举报






3

潘天坤 2024-12-27 17:15 20 [回复]举报

走道净高二分之一以上即为有效自然排烟,所以此内容可以与挡烟垂壁的设置无关

净高受限的走道如果需要划分防烟分区,确实比较麻烦,要满足不小于500毫米要求,又要满足疏散净高要求,这种情况可能考虑设置门洞或者开孔率大于25%的通透性吊顶会好一些

小唐12321   回复: 潘天坤2024-12-27 17:23

上次哪里看到疏散走道不能增设门

0    0 [回复]举报

潘天坤   回复: 小唐123212024-12-28 21:27

不上锁,不影响疏散的门一般没影响,或者设置梁或者门洞也是可以的

0    0 [回复]举报