消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

请问消火栓系统平时末端试水装置最大最小静压是多少?谢谢

请问消火栓系统平时末端试水装置最大最小静压是多少?谢谢

阿进 | 2024-12-15 19:18
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

小唐12321 2024-12-16 09:14 00 [回复]举报

5.2.2 高位消防水箱的设置位置应高于其所服务的水灭火设施,且最低有效水位应满足水灭火设施最不利点处的静水压力,并应按下列规定确定:     1 一类高层公共建筑,不应低于0.10MPa,但当建筑高度超过100m时,不应低于0.15MPa;     2 高层住宅、二类高层公共建筑、多层公共建筑,不应低于0.07MPa,多层住宅不宜低于0.07MPa;     3 工业建筑不应低于0.10MPa,当建筑体积小于20000m³时,不宜低于0.07MPa;     4 自动喷水灭火系统等自动水灭火系统应根据喷头灭火需求压力确定,但最小不应小于0.10MPa;     5 当高位消防水箱不能满足本条第1款~第4 款的静压要求时,应设稳压泵。

柠檬圈 2024-12-16 10:45 00 [回复]举报

消火栓系统是最不利点消火栓,不叫末端试水装置(喷淋系统的),一般装在屋顶,设有稳压泵的情况下静压应大于0.15Mpa,只设有高位消防水箱,参照栓规5.2.2条;最大静压看最有利点消火栓,不应大于1Mpa。

溜达呀 2024-12-16 11:33 00 [回复]举报

消火栓系统没有末端试水装置,在水力最不利处设置一个试验消火栓,如果你的系统设置了稳压系统,那么在试验消火栓处的静压不小于0.15Mp

 

关闭

关闭

手机APP下载