有顶步行街内小于300方的商铺,各商铺之间的防火隔墙上能不能用防火卷帘代替?或局部开口用防火卷帘代替?

有顶步行街内小于300方的商铺,各商铺之间的防火隔墙上能不能用防火卷帘代替?或局部开口用防火卷帘代替?

北洼 | 2021-04-10 13:43
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

牛疼 2021-04-11 11:20 01 [回复]举报

可以,但应满足建规6.5.3的相应要求。

消防网友76443 2021-04-12 16:51 00 [回复]举报

步行街两侧建筑的商铺之间应设置耐火极限不低于2.00h的防火隔墙,不能用防火卷帘代替。

北洼   回复: 消防网友764432021-04-13 11:13

规范上哪里有没有明确的依据?,我就是找至依据说不能用

0    0 [回复]举报

宾尼   回复: 北洼2021-04-14 11:41

建规第5.3.6.3条规定:步行街两侧建筑的商铺之间应设置耐火极限不低于2.00h的防火隔墙,每间商铺的建筑面积不宜大于300m²。

0    0 [回复]举报

北洼   回复: 宾尼2021-04-15 08:44

这条没有明确不能防火卷代替啊?

0    0 [回复]举报