消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

担负多个防火分区防护的泡沫—水喷淋系统中泡沫液用量如何确定?

担负多个防火分区防护的泡沫—水喷淋系统中泡沫液用量如何确定?

消防网友32388 | 2024-11-14 09:13
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 1

陈泽平 2024-11-14 10:28 00 [回复]举报

根据规范计算:泡沫灭火系统技术标准 GB50151-2021


3.2.2 保护非水溶性液体的泡沫-水喷淋系统、泡沫枪系统、泡沫炮系统泡沫液的选择应符合下列规定:
    1 当采用吸气型泡沫产生装置时,可选用3%型氟蛋白、水成膜泡沫液;
    2 当采用非吸气型喷射装置时,应选用3%型水成膜泡沫液。



6.1.3 泡沫-水喷淋系统泡沫混合液与水的连续供给时间应符合下列规定:
    1 泡沫混合液连续供给时间不应小于10min;
    2 泡沫混合液与水的连续供给时间之和不应小于60min。


6.3.4 闭式泡沫-水喷淋系统的作用面积应符合下列规定:
    1 系统的作用面积应为465㎡;
    2 当防护区面积小于465㎡时,可按防护区实际面积确定;
    3 当试验值不同于本条第1款、第2款规定时,可采用试验值。


6.3.5 闭式泡沫-水喷淋系统的供给强度不应小于6.5L/ (min • ㎡ )。

关闭

关闭

手机APP下载