水喷雾系统备用泵的问题

6.0.9 水喷雾灭火系统供水泵的动力源应具备下列条件之一:  

   1 一级电力负荷的电源;   

   2 二级电力负荷的电源,同时设置作备用动力的柴油机;   

   3 主、备动力源全部采用柴油机。


是不是三级及以下负荷的话主泵和备泵都是需要使用柴油机?

我的三江 | 2024-11-05 10:35
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

张治福 2024-11-05 16:51 00 [回复]举报

三级负荷就不需要双电源了,单电源就行了。

《民用建筑电气设计标准 GB51348-2019》

3.2.12 三级负荷可采用单电源单回路供电。