消防问答 > 消防给排水 提问

湿式自动喷水灭火系统和室内消火栓稳压系统,分别独立设置,高位消防水箱出水干管上的流量开关启泵的值设置多少合适?

湿式自动喷水灭火系统和室内消火栓稳压系统,分别独立设置,高位消防水箱出水干管上的流量开关启泵的值设置多少合适?

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 4 回答

消防网友21223 23-09-09

【消防给水及消火栓系统技术规范 GB50974-2014】→12.2 进场检验

12.2.8 压力开关、流量开关、水位显示与控制开关等仪表的进场检验,应符合下列要求:

4 流量开关应能在管道流速为0.1m/s~10m/s时可靠启动,其他性能宜符合现行国家标准《自动喷水灭火系统  第7部分:水流指示器》GB 5135.7的有关规定;


且:泄漏量<流量开关启动流量<泄漏量+1个喷头(或消火栓的流量)

0 0 [回复]举报

张治福   回复: 消防网友2122323-09-09

感谢,下次去工程上去实际应用一下。

1 0 [回复]举报

高工1986 23-09-11

江西省建设工程勘察设计协会文件给的值是2.33L/S。 窃以为应该是1.33+1.0的取值。


1 0 [回复]举报

一笑而过1   回复: 高工198624-06-01

老师,能解释一下吗?


0 0 [回复]举报

最新问题

关闭

关闭