消防问答 > 安全疏散 提问

7层工业建筑,其防烟楼梯间的最高层出口不设门是否合规?

7层工业建筑,其防烟楼梯间的最高层出口不设门是否合规?

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 3 回答

安洪全 23-07-11

如果是采用自然通风的防烟楼梯间,在最高处的出口不设门算合规。


建筑防烟排烟系统技术标准 GB51251-2017

3.2.1 采用自然通风方式的封闭楼梯间、防烟楼梯间,应在最高部位设置面积不小于1.0㎡的可开启外窗或开口;当建筑高度大于10m时,尚应在楼梯间的外墙上每5层内设置总面积不小于2.0㎡的可开启外窗或开口,且布置间隔不大于3层。


当然此条已被通用规范废止,算不上依据,但原理上是合规的。

1 0 [回复]举报

同同不同   回复: 安洪全23-07-11

这位兄台的疑惑应该是直通屋面的门设不设吧,如果是可以不设,除住宅每个单元一部疏散楼梯的情况需通过屋面连通,其他都不少于两个出口也没有通过屋面连通的放宽

0 0 [回复]举报

消防网友71978   回复: 安洪全23-07-12

楼上反贼先生讲的有道理,谢谢!

0 0 [回复]举报

最新问题

关闭

关闭