消防问答 > 火灾自动报警 提问

多线控制盘与总线控制盘的设置

多线控制盘与总线控制盘的设置问题,

火灾自动报警系统设计及验收规范,对多线直接控制有比较明确的要求,

如:喷淋泵、消防泵、防排烟风机,干式,预作用阀等设置多线直接启动


问题,那些设备需要置总线控制盘启动?

多线控制盘的,都要再有一套总线控制盘启动,



消防广播,电梯迫降,防火卷帘,送、排烟口,电动自然排烟窗等等,那些需要,依据条款是什么?
 消防

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 6 回答

查规范 21-12-11

你看看  自动报警系统规范吧,里面都有详细的说法


比如:火灾自动报警系统设计规范 GB50116-2013 >

4.3.2 手动控制方式,应将消火栓泵控制箱(柜)的启动、停止按钮用专用线路直接连接至设置在消防控制室内的消防联动控制器的手动控制盘,并应直接手动控制消火栓泵的启动、停止。

0 0 [回复]举报

阳光哥哥 21-12-14

总线 与多线是两个独立系统,不相互控制,各自成为一套系统

0 0 [回复]举报

好的哥 21-12-18

我又不知道说什么

0 0 [回复]举报

林继青 21-12-20

强切、警报、迫降总线控制盘启动

0 0 [回复]举报

天天消防 22-05-19

多线总线其实都可以设置的,但一些重要的消防设备一般都采用多线直接控制,就是在火灾控制器出问题的时候也能手动直接控制线场设备启动的。总线是靠主机总线去启动的,主要是声光广播强切电梯之类的控制器拿信号线控制的设备


0 0 [回复]举报

EHS专家-DL 25-03-14

《火灾自动报警系统设计规范》(GB50116)明确消防联动控制器需通过总线模块控制电梯迫降、防火卷帘、应急广播等设备‌。


在消防项目中,往往两者均需要设置,体现了系统冗余性、联动控制可靠性及现行规范要求,确保关键设备具备双重控制保障。

0 0 [回复]举报

最新问题

关闭

关闭