稳高压供水一定要稳压泵么

请问一下稳高压供水,一定要用稳压泵么?

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 4 回答

wanqc 21-09-10

如果建筑本身的水压满足要求就不用设置,但规范要求最不利点消火栓静压为一类高为1,大于100M为0.15,二类高和多层为0.07.

0 0 [回复]举报

刘丽波 21-09-10

稳高压,不是常高压,是需要稳压装置的。

1 0 [回复]举报

音鬼 21-09-17

稳高压系统是利用客观条件形成长期可靠的自然压力,这种系统别说稳压泵,水泵都可以不需要,前提是静动压满足规范要求,不满足的话就需要增设。

0 0 [回复]举报

横行霸道的螃蟹 21-11-03

现在规范不叫稳高压一说,只有临时高压一说

0 0 [回复]举报