消防问答 > 消防给排水 提问

消防取水口是否应设置防坠网

现在工程验收时,专家提出消防取水口应设置防坠网,有出处吗?个人认为不应设置防坠网,理由是消防取水口应上锁,已有安全保障措施,且施工图集也没有要设防坠网,且设置反而影响消防取水

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 4 回答

EHS专家-DL 25-03-21

我个人认为专家提出消防取水口设置防坠网是有一定道理的。虽然《消防给水及消火栓系统技术规范》GB50974未直接提及防坠网‌要求,施工图集和规范更多关注取水口的功能性要求(如吸水能力、标识清晰),而非防坠落措施‌等。但从风险预防防护功能冗余设计等思路,设置防坠网无疑更加安全。理由如下:

1、取水口若为敞口式设计(如井口),存在人员或杂物坠入的风险,类比井盖事故案例,增设防坠网可降低意外伤害概率‌。即使取水口上锁,仍可能因管理疏忽(如未及时锁闭)或外力破坏导致安全隐患‌。

2、防坠网作为物理屏障,可双重保障:既防止坠落,也阻挡杂物堵塞(尤其对未设置顶盖的取水口)‌。防坠网设计与消防功能不冲突,可采用可拆卸式网盖(如弹簧锁扣、铰链式网盖、不锈钢弹簧网等),确保消防取水时快速开启‌。

3、部分地区已将防坠落措施纳入验收要求(如西安、重庆)‌。

0 0 [回复]举报

重庆消防 25-03-21

0 0 [回复]举报

小唐12321 25-03-21

专家嘛,看权利,没权利就不理,有就按照,为了钱好拿,其实上锁就可以了。

0 0 [回复]举报

消防网友26453 25-03-25

查看图集  按图集做法

0 0 [回复]举报