消防问答 > 安全疏散 提问

请教下各位大佬,办公建筑套间内的走道是否还需要按双面布房1.5M设计?

请教下各位大佬,办公建筑套间内的走道是否还需要按双面布房1.5M设计?

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 8 回答

jinyanwu 24-12-31

个人意见,仅供参考:

根据《建规》:

1.1米即可,如果是高层,双面布房,1.4m。

同时考虑通规:

根据人数计算宽度。和上面的值比较一下,取大值。

0 0 [回复]举报

消防检查 24-12-31

房间内只有疏散距离的要求,疏散走道的宽度不适用房间内部。

1 0 [回复]举报

云中飞翔 24-12-31

最新规范规定,疏散走道宽度不小于1.1米

0 0 [回复]举报

本安消熊 24-12-31

《建规》5.5.18条已经废弃,个人建议执行《通规》即可7.1.4条第3款:疏散走道、首层疏散外门、公共建筑中的室内疏散楼梯的净宽度均不应小于1.1m;同时满足《通规》7.4.7条文即可。

个人意见,仅供参考!

0 0 [回复]举报

小唐12321   回复: 本安消熊25-01-02

建规5.5.18哪里看到已经废止了

0 0 [回复]举报

本安消熊   回复: 小唐1232125-01-21

通规前言:


0 0 [回复]举报

本安消熊   回复: 本安消熊25-01-21

也同时要满足《办公建筑设计标准》JGJ/T67-2019

0 0 [回复]举报

vicher 25-01-02

新的建筑设计防火标准尚未颁布,《建筑设计防火规范》GB5016-2014相关条文仍为消防设计及审查的指导性文件。有关办公楼走道宽度要求见《建筑设计防火规范》GB5016-2014第5.5.18条及《办公建筑设计标准》JGJ/T67-2019第4.1.9条相关规定。


0 0 [回复]举报

最新问题

关闭

关闭