消防问答 > 消防给排水 提问

关于消防水泵至消防水池间管段压力的问题

请问各位专家老师,消防管网有压力,但是消防水泵至消防水池之间压力表压力值为0,且阀门都处于开启状态,是什么原因?正常吗?

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 8 回答

周家斌 24-11-01

此段管道压力较低,选用的压力表型号或精度不足,测(显示)不出压力的。

0 0 [回复]举报

消防小萌新   回复: 周家斌24-11-04

老师您好,现场两台电动泵出水管压力位0.3MPA,2台消防水泵至消防水池管段压力表读数都为0,我现场看了下,消防水泵出水管和进水管的压力博鳌都是同一种型号,消防水池距离地面4米高,距水泵高度基本在3.5米左右,消防水池400立方

0 0 [回复]举报

大悟无言 24-11-01

水泵吸水管吗?那一段没有经过水泵加压,是没有什么压力的,基本就是消防水池的水压那么大点。

0 0 [回复]举报

消防小萌新   回复: 大悟无言24-11-04

老师您好,现场两台电动泵出水管压力位0.3MPA,2台消防水泵至消防水池管段压力表读数都为0,我现场看了下,消防水泵出水管和进水管的压力博鳌都是同一种型号,消防水池距离地面4米高,距水泵高度基本在3.5米左右,消防水池400立方

0 0 [回复]举报

小罗!!! 24-11-03

那个是真空表

0 0 [回复]举报

消防小萌新   回复: 小罗!!!24-11-04

消防进水管和出水管管道压力表相同,出水管上压力表读数时0.3,进水管是0

0 0 [回复]举报

嘻嘻哈哈消防 24-11-05

实际应该有一点点压力,非常小,压力值为水池水位至水泵进水管的高差,也就0.03-0.04mpa左右,压力表指针起伏非常小。第二就是阀门坏了,外观看着是开启状态,实际内部没开启,压力表就是0了。

0 0 [回复]举报

jinyanwu 24-11-15

一般管道上都有止回阀,管网有压力说明系统可能有稳压泵和稳压罐(或者消防水池位置较高,或者管道在市政管网上连着,管道上保持管网压力),维持系统压力,当系统出现情况(火灾或者泄漏或者试验等情况),相当于开启中间阀门,稳压罐出水,压力降低到一定程度时稳压泵增压供水,供水量不能满足要求时系统压力继续降低,则消防泵启泵。

平时压力表上示值应该为0.04Mpa,不好看出来。

0 0 [回复]举报

最新问题

关闭

关闭